finster1
Member
- Location
- New Jersey
I was working in a restaurant and the 1200a main kept tripping instead of the branch circuits. Generator auto transfer kept tying back in...Having hard time locating source of problem. POCO Line voltage good 208v 3ph y...Shutdown main components running on three phase but still tripping....Restaurant active and needed some life line to a restaurant devices so I shut off what I could and still tripping. Even shutdown ac units still tripping. Many subpanels 400a 225a, 200a some 100a at least 10 separaTE SUB SYSTEMS. sIEMENS BREAKER 1200a main. Tryed reading to ground lines off breakers but with devices still attached and restaurant still operable kind of tough...Any suggestions. Left and told manager to continue to shutoff main 1 at a time untill he gets to the point that one of them doesn't cause a trip and that if all elkse fails maybe the shunt trip in the main was starting to fail of the shunt was being sent from the generator for some reason., but the timing of the trip usually 4 to 5 minutes after resetting made me believe it was from a faulty component in the kitchen or an ac unit