I ran into an interesting problem at a facility and thought I would post it here for discussion.
The facility has (3) 1200A 277/480V 3 phase 4 wire switchboards that are all located in different areas of the building. All the switchboards are fed from the same 4000A main switchboard. Each board is fed with (3) individual sets of 4#500, which includes a full size neutral, through 4" PVC conduits in a concrete ductbank. A single 3/0 ground wire originates from the main 4000A switchboard and is run through a separate adjacent conduit in the ductbank and then connected to the 1200A switchboard. It appears that this was done during the original construction in the early '70's.
I have reviewed both the NEC and Mike's Grounding verses Bonding book and believe the only solution is to (1) remove the existing 500 feeders, (2) remove the single 3/0 ground wire, and (4) pull 3 new sets of 4#600, EACH with (1) 3/0 ground.
Am I missing anything here?
Tom
The facility has (3) 1200A 277/480V 3 phase 4 wire switchboards that are all located in different areas of the building. All the switchboards are fed from the same 4000A main switchboard. Each board is fed with (3) individual sets of 4#500, which includes a full size neutral, through 4" PVC conduits in a concrete ductbank. A single 3/0 ground wire originates from the main 4000A switchboard and is run through a separate adjacent conduit in the ductbank and then connected to the 1200A switchboard. It appears that this was done during the original construction in the early '70's.
I have reviewed both the NEC and Mike's Grounding verses Bonding book and believe the only solution is to (1) remove the existing 500 feeders, (2) remove the single 3/0 ground wire, and (4) pull 3 new sets of 4#600, EACH with (1) 3/0 ground.
Am I missing anything here?
Tom