I am bidding on a job to install 20' of 480v 3-wire bus rail with a 1200amp tap box. I am using 4" rigid conduit. I am running 3 seperate conduits, each with 3 500MCM THHN's and 1 3/0 THHN ground. According to Table 310-16 500MCM THHN is rated at 430amps if there are not more than 3 current carrying conductors in the conduit. Should I run 4 sets of 500MCM for this 1200amp bus or will the three be enough. I get 1290amps with three runs. The breaker will be 1200 amps. They cannot use 1200amps because they will exceed 80% of the breaker and have tripping problems.
 

benaround

Senior Member
Location
Arizona
Elvis,

500mcm is good for 380amps in the 75deg column, you can't use the 90deg

column unless all terminations are rated for 90deg. , which I'm told are very

rare indeed. You can use the 90deg. column for derating.

3x380=1140amps if the load is 1140a or less 3 runs will work, if the full 1200a

is expected you need to figure another way.
 