120v/240v Panel

Status
Not open for further replies.

templdl

Senior Member
Location
Wisconsin
I do very little residential work. Using a 2P breaker is considered 208V single-phase, not 240V. 240V sounds weird to me.

The only way that I'm aware of in order to get 208 single phase is with a 208 y/120 3ph4w supply. With this system you can feed a 208 1ph2w load from the line to line. To do this you would install a 2p breaker in a 208y/120 3ph4w panel. .for 120v 1ph2w from a line to neutral you instal a 1p breaker which would proved 120 between that line and the neutral.
 

ASG

Senior Member
Location
Work in NYC
Occupation
Electrical Engineer, PE
The only way that I'm aware of in order to get 208 single phase is with a 208 y/120 3ph4w supply. With this system you can feed a 208 1ph2w load from the line to line. To do this you would install a 2p breaker in a 208y/120 3ph4w panel. .for 120v 1ph2w from a line to neutral you instal a 1p breaker which would proved 120 between that line and the neutral.

Correct. This is what I do almost exclusively in commercial spaces. Pretty much nothing is 240V.
 

kwired

Electron manager
Location
NE Nebraska
Maybe in your area, but for many of us Deltas are pretty common.

And there is a lot of smaller (load wise anyway) commercial spaces that are just supplied with single phase 120/240 volts.

I have been around school buildings, nursing homes, retail stores, churches, with 400, 600, 800 amp single phase services.

Converted a few of them to three phase as well when they decided to build additions or add major loads.
 