Re: 120v 277v insame 3ph box
Let me try and rephrase the question. You come upon a 3-phase panelboard. You measure voltage from each of the three main lugs to ground. What you get is 120 volts from Phase A to Ground, 120 volts from Phase B to Ground, and 277 volts from Phase C to Ground. The question is this: "Can this panelboard have been connected properly, in accordance with the NEC, and still get these three readings?"
terrytc: Did I get your question right?
To the rest of the membership: I am not familiar with "high leg delta," and that might not even be the right name. But if you have a delta secondary, with phase to phase secondary voltage at 240volts, and if you connect the center of one secondary winding to ground, will this not give you the voltage readings that terrytc is asking about?