pierre
Senior Member
- Location
- Westchester County, New York
Re: 120v 277v insame 3ph box
"Having the neutrals tied together in the panel will not cause any problems. It happens on every code compliant installation where there are two or more systems with grounded conductors in a building. All of the grounded conductors are tied together by the system bonding jumpers and the grounding electrodes.
Don "
Are you saying that there is continuity between the neutral conductor of a 120v system and a 277v system that are in the same building?
"Having the neutrals tied together in the panel will not cause any problems. It happens on every code compliant installation where there are two or more systems with grounded conductors in a building. All of the grounded conductors are tied together by the system bonding jumpers and the grounding electrodes.
Don "
Are you saying that there is continuity between the neutral conductor of a 120v system and a 277v system that are in the same building?