You should power this circuit through auxiliary contacts.
Your 480:120 xfmr is required to have protection. At 50VA puts it under 2A on primary. Being a 2-wire secondary you can use primary only protection... but it cannot be greater than 300%, which is 50VA÷480V×300%=0.3125A.
Are you certain you only need a 50VA xfmr? What's the rating of the louver motor?
Thank you for the feedback.
The louver motor is 30W.
There is a separate intake louver for each exhaust fan. We ran circuits utilizing the aux contact for those. The exhaust fan louvers are co-located to the motor. Utilizing the trf will save us running new circuits.
Does article 725 apply? That is where I was getting 500% (430.72(c)(4) . 500vs300% is really negligible but I was more curious.