221110-2100 EDT
dw85745:
Some basic information to work from.
A single phase motor fed from a single phase source will not self start mechanical rotation. It will just sit nearly still, but you will feel or hear it vibrate. It can be started by some external applied rotation, a rope and pullly, or something else to momentarily drive the rotor.
To electrically start a single phase motor you need some electrical scheme to produce some limited sort of rotating magnetic field. Thus, at least for starting purposes the motor needs to be at least a 2 phase motor. There are various ways to accomplish this.
The circuit shown by ptonsparky consisted of two phase shifting circuits. One circuit is a capacitor and another coil that is not the main power coil. This circuit is present both during starting, and running. The second circuit adds more capacitance in parallel with the first capacitor ( more starting torque ) just during starting ( in some fashion with some time delay to opening ) .
I don't believe this normally closed contact in series with the starting capacitor is voltage controlled from something relating to starting voltage unless the relay contact also has a time delay function.
.
dw85745:
Some basic information to work from.
A single phase motor fed from a single phase source will not self start mechanical rotation. It will just sit nearly still, but you will feel or hear it vibrate. It can be started by some external applied rotation, a rope and pullly, or something else to momentarily drive the rotor.
To electrically start a single phase motor you need some electrical scheme to produce some limited sort of rotating magnetic field. Thus, at least for starting purposes the motor needs to be at least a 2 phase motor. There are various ways to accomplish this.
The circuit shown by ptonsparky consisted of two phase shifting circuits. One circuit is a capacitor and another coil that is not the main power coil. This circuit is present both during starting, and running. The second circuit adds more capacitance in parallel with the first capacitor ( more starting torque ) just during starting ( in some fashion with some time delay to opening ) .
I don't believe this normally closed contact in series with the starting capacitor is voltage controlled from something relating to starting voltage unless the relay contact also has a time delay function.
.