A typical flow switch has 2 sets of contacts, 1 for the Fire Alarm system and 1 set for a 120vac Horn / strobe to help the Fire Fighters locate the Siamese Connection on the building.peter d said:In my area, we have a local code that requires an exterior bell to ring during water flow. This is accomplished by using a 120 volt bell, controlled by a flow switch, or a mechanical bell that operates by the actual water flow.
Stallzer said:A typical flow switch has 2 sets of contacts, 1 for the Fire Alarm system and 1 set for a 120vac Horn / strobe to help the Fire Fighters locate the Siamese Connection on the building.
Billy_Bob said:Don't know if this helps or not...
I've seen 120V wired to a fire sprinkler flow switch, then this went to the main breaker to turn off power to the building. So fire sprinkler head pops, water flows in pipe, flow switch activates, power to building cut.
Billy_Bob said:Don't know if this helps or not...
I've seen 120V wired to a fire sprinkler flow switch, then this went to the main breaker to turn off power to the building. So fire sprinkler head pops, water flows in pipe, flow switch activates, power to building cut.
mdshunk said:Some of these replies make me think some guys don't know what a PIV valve is. It has nothing to do with indicating flow.
MichaelGP3 said:Are you sure that's what you were looking at?
You'll have to forgive me....while I've seen shunt trip coils used to trip a breaker to kill power to elevators (once the feedback signal has come back from the elevator controller indicating that the elevators are recalled and the doors are held open), and in computer rooms to shut down mainframes, incorporated into the suppression system, the concept of using one to shut off power to a building is new to me....
So, have there been many .... 'incidents' .... taking place during the required periodic testing of this particular system? Please tell me its not a hospital or a air traffic control tower or a nuclear power plant, or one of those nightclubs that gets packed to the doors on the weekends.....
Billy_Bob said:I'm darn sure the flow valve tripped the main breaker because my job at the time was testing fire alarms and I was testing the flow switch to be sure if one head popped, this would activate the fire alarm.
So when I tested the alarm by opening the test valve, the alarm triggered and the power went out!
Then I investigated and saw that the flow switch was also wired to the main breaker! This was a large national retail chain-store.
This store had refrigeration equipment to keep food for sale cold as well as A/C... I informed my boss about this unusual set-up with the fire sprinkler flow switch, then he met with his boss, etc.
This resulted in a letter to the retailer that we could no longer test the fire alarm flow switch unless they wrote us a letter saying we not responsible to any damage to any of their equipment (refrigeration) due to power loss from testing the alarm.
amps88 said:This has everyone confused, even our Fire Alarm Technician.
In on panel in a dining facility there is a 20A breaker indicated for a tamper switch and one for the PIV.
Why would someone run 120v to devices on the fire alarm loop?