Billy_Bob said:I'm darn sure the flow valve tripped the main breaker because my job at the time was testing fire alarms and I was testing the flow switch to be sure if one head popped, this would activate the fire alarm.
So when I tested the alarm by opening the test valve, the alarm triggered and the power went out!
Then I investigated and saw that the flow switch was also wired to the main breaker!
Sure sounds to me like you might have an Electrician that wired a Flow switch incorrectly. Since it's a normally open contact that's used on the switch, could it be possible that a Sparky landed both a hot and a neutral on the Flow switch ? Instead of using only the hot leg to be switched ?