Once you get up to the scale of multiple heaters (say a house with a bunch of electric baseboards heaters) you end up having to deal with load diversity maths.
A single resistance heater rated at 250V will have lower wattage when run at 230V. But in a house these heaters are being cycled on and off because of thermostats, and the total power being delivered has to average out to the heat load of the building. Same power at lower voltage means _higher_ current.
How do we reconcile that lower voltage into a resistor means lower current, but lower voltage into the house means higher current (for resistance heating)?
For the house to be at the same temperature, the same total BTU needs to be delivered. For an individual heater at lower voltage, the heater draws lower current, operates at lower power, and needs to run longer to deliver the same total BTU.
When you average across a bunch of heaters, each cycling on and off on its own thermostat, in aggregate delivering the same total BTU, the load diversity gets changed, and the aggregate average current must go up. So instantaneous current to an individual heater goes down as voltage goes down, but average aggregate current to the entire house goes up to deliver the same BTU per hour.
-Jon