120V UPS plugging into a 15A or 20A duplex

Status
Not open for further replies.

cppoly

Senior Member
Location
New York
In terms of connecting a portable UPS into a 15A or 20A duplex receptacle, are there any requirements that I need to be aware of?

1,700VA , 120V – can this plug into a 15A duplex receptacle or does it need to be 20A? Dedicated receptacle or no?

Thanks
 

retirede

Senior Member
Location
Illinois
Did the unit come with a factory cord/plug? If so, that’s the receptacle you can plug in to. The manufacturer’s instructions should specify if a dedicated circuit is required. It’s probably a good idea for that size load.
 

jap

Senior Member
Occupation
Electrician
Does it come with a 15 amp male cord end?

A dedicated receptacle outlet is singular.

A duplex receptacle is more than 1 place to plug in.

Jap.
 

jap

Senior Member
Occupation
Electrician
Did the unit come with a factory cord/plug? If so, that’s the receptacle you can plug in to. The manufacturer’s instructions should specify if a dedicated circuit is required. It’s probably a good idea for that size load.

You beat me to it. :)

JAP
 

cppoly

Senior Member
Location
New York
I have to check the 15A or 20A cord end.

My concern that I'm thinking of though is that since the load is 1,700VA and if the batteries are charging (could be 2A up to 8A I've seen on some data sheets) then wouldn't the 1,700VA + 960VA (8A charging) overload the circuit? I know it would only be temporary to bring the batteries up to full charge. But still a concern?
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
I have to check the 15A or 20A cord end.

My concern that I'm thinking of though is that since the load is 1,700VA and if the batteries are charging (could be 2A up to 8A I've seen on some data sheets) then wouldn't the 1,700VA + 960VA (8A charging) overload the circuit? I know it would only be temporary to bring the batteries up to full charge. But still a concern?
The UPS probably doesn't work that way. Check its documentation. My guess is that it can output 1700VA but never draws more than 8A from the receptacle for charging, no matter what you're using. But check the documentation.
 

jap

Senior Member
Occupation
Electrician
I have to check the 15A or 20A cord end.

My concern that I'm thinking of though is that since the load is 1,700VA and if the batteries are charging (could be 2A up to 8A I've seen on some data sheets) then wouldn't the 1,700VA + 960VA (8A charging) overload the circuit? I know it would only be temporary to bring the batteries up to full charge. But still a concern?

I never look that far into it.

The manufacturer should have all that covered with the type of cord and male end that it comes with.

JAP>
 

jap

Senior Member
Occupation
Electrician
With all that being said, you could still overload the circuit because it doesn't take into consideration what all else may be plugged into that circuit.

JAP>
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
. . . since the load is 1,700VA . . .
But it isn't. That's the battery/inverter capacity. The load is whatever the UPS is powering.

The battery recharging current is typically 1/10 of its capacity, and 1/10 of that at 120v.
 

cppoly

Senior Member
Location
New York
Thanks.

Does 210.21(B)(2) or 210.23(A)(1) 80% max load for cord and plug come into play at all? Even though the UPS is supplying multiple outlets and no individual piece of equipment connected to the UPS would exceed the 80% rating of the circuit, could an argument be made that a UPS is a a "singular" cord and plug load (since you are plugging in a singular UPS plug into a duplex receptacle) and I would have to comply with this?
 

jap

Senior Member
Occupation
Electrician
Thanks.

Does 210.21(B)(2) or 210.23(A)(1) 80% max load for cord and plug come into play at all? Even though the UPS is supplying multiple outlets and no individual piece of equipment connected to the UPS would exceed the 80% rating of the circuit, could an argument be made that a UPS is a a "singular" cord and plug load (since you are plugging in a singular UPS plug into a duplex receptacle) and I would have to comply with this?

Does the label on the UPS unit actually indicate that the input current is 14.17 amps?

JAP>
 