Well some stackable washer dryers use 240v
(But) they need a insulated neutral for the 120 part of machine ( washer motor
You need to check paper work to be sure
Sent from my iPhone using Tapatalk
If you do a deeper dive into some of those listings (such as Electrolux) you will see the statement that the models are "not designed for use in North America" and there is no mention of UL listing.
So the devil is in the details on a machine by machine basis.
For a given machine, this may just be CYA, or it could also reflect the fact that the machine is designed to have one of the 220V input lines be a grounded conductor. Or that the necessary UL testing was not done since it is not helpful in the intended market.
The possibly required laundry circuit is now a 240 volt non-MWBC circuit fed from a two pole breaker. Does that still meet the requirement for a laundry circuit?
Tapatalk!
210.11(C)(2) Laundry Branch Circuits. In addition to the number
of branch circuits required by other parts of this section, at
least one additional 20-ampere branch circuit shall be provided
to supply the laundry receptacle outlet(s) required by
210.52(F). This circuit shall have no other outlets.
210.52(F) Laundry Areas. In dwelling units, at least one receptacle
outlet shall be installed for the laundry.
Here, in UK, and in the EU zone everything residential runs on 230V single phase. It keeps things simple. One system. I think a lot of people here would be perplexed/horrified to be confronted with something like a washing machine that needed two different voltages.Ah...very interesting. Can't say I have run into them and in my mind I began to think...why on earth would you need a 240V washing machine but as someone else posted I guess they have an onboard water heater...go figure.
Wow, thanks guys for all the replies. I have more information.
It is a Bosch Wap24202uc, 2.2 cuft. I had to wait for the my old man to wake up. Ok so it sounds like I am good to go.
1) So just to be clear, it does not matter that the circuit is originating off a panel with grounded and and grounding conductors that are separated because no neutral is needed on washer, correct?
2) And I am assuming that if the washer did require a neutral, converting existing line to 240v and bonding the grounding and grounded terminals would in fact be a violation because of the type of panel it is, correct?
2) This is also correct-- but this is for dryers not washers.
Same for stoves?
We do have a neutral.I believe the dryers in Europe are also 240 or 230 but they do not have a neutral and are 20 amps. I have installed one of those. I am wondering when they are going to make the american units straight 240.
European equipment will never have a 220/110 type of wiring since all they have in a house is 220 50hz
So everything on them runs at 220v, some areas of Europe do not have a grounded system and depend upon RCD's to protect from shock hazards, but the biggest problem is two fold, the motor will run faster, and if it has an older synchronous or an electronic timer that depends upon the frequency of the power line then the clock will run faster on 60hz, so it just goes through its cycles faster, but then the agitator and spin cycles also run faster.
My sister has a whirlpool front loader that is also 240 volts 60hz rated, it did not need a neutral, the matching dryer which was also 240 volts, unlike older units also did not need a neutral as everything including the timer and motor was 240 volts, I just did like was said here, since she had NM I remarked the whit black on both ends and changed the receptacle to a 250v 15/20 amp, it had one slot that looked like a sideways T because the 15 amp is two side ways flat blades and the 20 amp is one vertical and one sideways.
But you must check the manufactures specs, if you have the model number, maybe we can look it up for you since you can't get it to load?