125 amp sub panel wire size

Status
Not open for further replies.

Stevenfyeager

Senior Member
Location
United States, Indiana
Occupation
electrical contractor
House has outside 125 amp disconnect. House sub panel cannot use the typical residential service cable size because inspectors here say it’s not a ‘service’. Please help me determine which column to use for my cable size. I need a 4 conductor cable. Existing is 3 wire #2 Cu cable so I have to replace it. If I am reading the correct column, even their #2 was too small. Thanks!
 
Is there just the one 125 amp service disconnect feeding this one panel ?
If so, a #2 Cu or 1/0 AL will work.
 
I’m sorry, my inspector says it is still considered a service. I was confusing times when I have to add a 100 amp sub panel and I can’t use my usual residential service size #2 AL. Sorry.
 
If the house panel serves the entire load of the dwelling, then you can use the ruduced table for a dwelling and the #2 is sufficient.
 
I’m sorry, my inspector says it is still considered a service. I was confusing times when I have to add a 100 amp sub panel and I can’t use my usual residential service size #2 AL. Sorry.
It's a feeder to the sub-panel not a service.

For a 100 amp sub-panel that is not carrying the entire load then the feeder conductors are sized according to T310.15(B)(16) so #2 Al is only good for 90 amps.
 