At one point, 705.12 specified the interconnection breaker rating. As of 2014, they rewrote it in a way that no longer requires you to use the breaker rating, but rather the calculation that determines it, prior to rounding to the breaker you actually use. This stops rounding errors from being a show-stopper.
One example where it would govern a design decision:
You have a 600A panel with a 600A main. This gives you 120A of headroom for interconnecting. Prior to the rewrite in 2014, this would limit you to a 110A interconnection breaker which corresponds to 88A of output current from your inverter(s). With the wording in NEC 2014, this would allow for up to 96A of output current from your inverter(s), which you'd have to land on a 125A breaker. A 125A breaker would not meet the rule prior to 2014, but now it does.
Another example:
You have a critical loads panel, with a battery backup inverter. This is a 100A subpanel that passes through the battery inverter's transfer switch, which is normally supplied from a 200A main panel with a 200A main breaker. You connect a 40A PV inverter to this critical loads panel, which follows the battery inverter during off-grid mode. Prior to 2014, you'd be limited to providing your subpanel and critical loads with no more than a 40A breaker, which extremely limiting. With the 2014 rewrite, the fact that the 100A breaker has a 100A rating, is irrelevant to the rule. You are only backfeeding 40A/(125%) worth of inverter current, even if a larger breaker is part of its path.