Voltage drop is a must learn for any person in the electrical field, even though it is an FPN in the NEC and not enforceable,
I was told that your only allowed something like a 3 percent difference in "acceptable voltage" versus "allowed voltage" or "120V" versus "115" or something to that effect. Thus being enforceable, no?
Jay, you seem to have had good explanations now, but I'll add another situation.So the wire only needs to be #10 until it gets close to the receptacle? Then it doesn't matter any more? That doesn't sound right. Either you need larger wire or you don't.
I was watching a rerun Holmes on Homes, and his electrician was redoing a panel and made a big deal out of the fact that the panel was holding all 15A breakers and there were 12AWG romex coming out of it. "Where are these connecting to?" He says afterwards.
1)Is it not allowed for 12AWG romex to connect to a 15A breaker?
2)If not, what would you do if you needed larger gauge wire for voltage drop?
Voltage drop is a must learn for any person in the electrical field, even though it is an FPN in the NEC and not enforceable
He's not a real electrician, he just plays one on TV.:grin:
(See post #16.But he did stay at a Holiday Inn Express last night.![]()
(See post #16.)
Probably because the top section, where the service/feeder enters, has a separate enclosure. They're protected from contact with the incoming conductors.I watch that show also , and have you noticed that most of the electrical panels shown in the shows have all the branch circuits coming in on both sides of the panel an hardly ever enter from the top of the panel.
Just curious is to why they do that and it looks funky to me.