Greetings Ladies and Gentlemen: I am stumbling. I am not particularly familiar with impedance grounded, 13.8kv, SDS.
Existing Installation:
The service is 138kv. The substation xfm belongs to the customer. xfm is 20MVA, 8%, 138D/13.8Y, impedance grounded, 167ohm. 500' of 3 parallel - 3c/350CU w/#2 g, MC-HL to 13.8 OCP. xfm sec OCP is 800A. The MC-HL sheaths are terminated at the OCP end and are not terminated at the xfm end. Yes, they should have been, but they aren?t. I am told the plan is to eventually terminate the sheath - not sure how, it would be very difficult to get a TMC fitting over the conductors. (However, that is another issue)
Q: What code section(s) determine(s) the size of the grounding conductor from the xfm to the OCP?
Here are my thoughts:
1. It's not a service, it's an SDS.
2. So, starting at 250.30, Exception: sends us to 250.36 or 250.186.
3. 250.36 is for 480 to 1000V, so that doesn?t fit
4. 250.186 Impedance Grounded Neutral Systems, kv and over, shall comply with:
A. Location - okay we are there
B. Identified and insulated - okay done
C. System neutral connection point - okay
D. Equipment grounding conductors. ?EGCs shall be permitted to be bare, and shall be electrically connected to the ground Bus and grounding electrode conductor.?
Humm. Nothing about the size.
The next place we get a clue is:
5. 250.190, Grounding of Equipment, ?All non-current carrying metal parts ? shall be grounded.? Still nothing about size.
I?m thinking the code is telling me there shall be an EGC, but I have to pick the size. Which makes sense, one might think at 13.8kv the installations are engineered, not cookie cutter.
Engineeringly speaking, the grounding impedance limits the current to 47A. The protective relays take the xfm out in a second or so. The installed #2 in each cable is sufficient
The real problem:
I have a third party inspector (not an AHJ - but with sufficient corporate support we will be mandated to follow) that is suggesting the grounding conductor from the substation xfm to the OCP should meet 250.122. Which would mean a 1/0 for an 800A CB. (I?d likely size for a 1000A CB, just cause we could set the CB up to that if future loads were added).
The cable armor (sheath) was not terminated at the substation end, so there is no credit for the extra grounding conductor equivalent cross sectional area. So, the installed #2 is small by 250.122 criteria.
carl
Existing Installation:
The service is 138kv. The substation xfm belongs to the customer. xfm is 20MVA, 8%, 138D/13.8Y, impedance grounded, 167ohm. 500' of 3 parallel - 3c/350CU w/#2 g, MC-HL to 13.8 OCP. xfm sec OCP is 800A. The MC-HL sheaths are terminated at the OCP end and are not terminated at the xfm end. Yes, they should have been, but they aren?t. I am told the plan is to eventually terminate the sheath - not sure how, it would be very difficult to get a TMC fitting over the conductors. (However, that is another issue)
Q: What code section(s) determine(s) the size of the grounding conductor from the xfm to the OCP?
Here are my thoughts:
1. It's not a service, it's an SDS.
2. So, starting at 250.30, Exception: sends us to 250.36 or 250.186.
3. 250.36 is for 480 to 1000V, so that doesn?t fit
4. 250.186 Impedance Grounded Neutral Systems, kv and over, shall comply with:
A. Location - okay we are there
B. Identified and insulated - okay done
C. System neutral connection point - okay
D. Equipment grounding conductors. ?EGCs shall be permitted to be bare, and shall be electrically connected to the ground Bus and grounding electrode conductor.?
Humm. Nothing about the size.
The next place we get a clue is:
5. 250.190, Grounding of Equipment, ?All non-current carrying metal parts ? shall be grounded.? Still nothing about size.
I?m thinking the code is telling me there shall be an EGC, but I have to pick the size. Which makes sense, one might think at 13.8kv the installations are engineered, not cookie cutter.
Engineeringly speaking, the grounding impedance limits the current to 47A. The protective relays take the xfm out in a second or so. The installed #2 in each cable is sufficient
The real problem:
I have a third party inspector (not an AHJ - but with sufficient corporate support we will be mandated to follow) that is suggesting the grounding conductor from the substation xfm to the OCP should meet 250.122. Which would mean a 1/0 for an 800A CB. (I?d likely size for a 1000A CB, just cause we could set the CB up to that if future loads were added).
The cable armor (sheath) was not terminated at the substation end, so there is no credit for the extra grounding conductor equivalent cross sectional area. So, the installed #2 is small by 250.122 criteria.
carl