130 feet of SER 4/0 Al. Have you run this long ?

Stevenfyeager

Senior Member
Location
United States, Indiana
Occupation
electrical contractor
130 feet of 4/0 SER Al from disconnect to 200 amp panel in house. I don't think I've installed a 200 amp residential panel that far from a meter disconnect before. Voltage drop on line calculator says 2.3 % drop. Does this sound ok ? Thanks.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Even at 200 amps you have less than 3% drop and as Larry says these loads are historically lower than the ampacity
 

marmathsen

Senior Member
Location
Seattle, Wa ...ish
Occupation
Electrical Contractor
It’s not hard just very labor intense. I hate that crap lol. Rather pipe it and pull if possible.
It really depends on the route. If you're able to pull through an attic or if it's going through a bunch of framing up and down through walls. Sometimes you need a bunch of people to help.

Rob G - Seattle
 