The 18/2 thermostat cable for the door controls is a class 2 circuit. It is not allowed in the box with the power circuit. There are some exceptions to this for class 2 circuits but they would not apply in this case. In any case I'm not sure why you even want to do this.I have always done this. Always passed the electrical inspection. i see many other new houses like this. The city building inspector does not think it is allowed. Thanks
The control wire for the door would have to have the same temperature rating as the 120V conductor.I have always done this. Always passed the electrical inspection. i see many other new houses like this. The city building inspector does not think it is allowed. Thanks
So it can give a cleaner look than a second box for lovo. It can get rolled up in the back of the box before the 120v, and then it's out of the way of the drywallers using a rotozip.I'm not sure why you even want to do this.
For what it's worth, I always nail on my receptacle box first, then I use the head of my hammer as a spacer to set the lovo box about an inch awayWell, it sounds like I shall change my future single gang garage door opener box to two boxes. 1 for 14/2, and 1 for 18/2. Thanks.
Bet you waste a lot of hammers leaving them stuck between boxes!For what it's worth, I always nail on my receptacle box first, then I use the head of my hammer as a spacer to set the lovo box about an inch away
Just a fast and easy way to space them the same every time
They make a 2 gang box. One side for 120 volt receptacle/ other side for low voltage. May be just as cost effective using two single gangs!For what it's worth, I always nail on my receptacle box first, then I use the head of my hammer as a spacer to set the lovo box about an inch away
Just a fast and easy way to space them the same every time
About $7.00Do they make a 2 gang cover, half receptacle, half blank?
I was wrong, this can't be used it's a fire rated ceiling.Or this low voltage 1 gang
More importantly, it would need to have the insulation voltage rating to be a minimum of the highest voltage in the box. Insulation voltages generally come in 3 levels for LV wiring: 50V, 300V and 600V. MM-B is 600V, so assuming your garage door is 120V that’s fine, but many low voltage (alarm and signal low) wires are 50V max, so cannot be in the same box. You CAN find 300V and even 600V signal wiring, you just have to look for it.The control wire for the door would have to have the same temperature rating as the 120V conductor.
A residential garage ceiling is not fire rated.I was wrong, this can't be used it's a fire rated ceiling.