donselectric

Senior Member
Location
nh
we are still on 05 code.
the reason for two circuits is
the guy wants 12 recpts,6 recessed and two ceiling fans
and i like to feed each room separate if possible
looks like the rooky pipe out side house or no afci...
 

Jim W in Tampa

Senior Member
Location
Tampa Florida
I sure dont like the idea of a panel in the attic. Even if it has stairs and meets 110.26 the heat will likely destroy the new arc faults. What are the chances of taking some of the load off of the attic light. That was a trick i used often to get out of a jam.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I sure dont like the idea of a panel in the attic. Even if it has stairs and meets 110.26 the heat will likely destroy the new arc faults. What are the chances of taking some of the load off of the attic light. That was a trick i used often to get out of a jam.

Is this an unconditioned space? It appears it is a bedroom , etc. The panel can be in the bedroom or den (whatever the other room is).

This brings me to ask how is this space being heated and/or cooled?
 

Jim W in Tampa

Senior Member
Location
Tampa Florida
Is this an unconditioned space? It appears it is a bedroom , etc. The panel can be in the bedroom or den (whatever the other room is).

This brings me to ask how is this space being heated and/or cooled?

ok i was not thinking of it that way. Sure if you put the panel in one of the rooms then i am cool with it. As to the heating and cooling perhaps the AC man can up size the unit.
 

M. D.

Senior Member
As far as heat goes ... don't some of you guys ,.. in the warmer parts of the country,.. install panels outside??
 

M. D.

Senior Member
sub panel... off what the 14/3 ??
cant do that...violation...branch circuit extension so i was years ago


I have trying to figure this out ,.. did you mean

"so was I years ago"
or

that someone has used this circuit to feed other outlets on the way to the attic??

If you do a load calc. I would be surprised if it required 2 circuits.

As far as the sub panel goes ,.. what is the concern???
 

donselectric

Senior Member
Location
nh
i got picked up on that years ago was told by inspector
that it was a branch circuit extension and i couldnt do it
so i dont do it...hmmm
 

M. D.

Senior Member
Well,.. I guess he never read the definitions of Feeder and branch circuit..
I think this is a fine idea,.. and will probably become a bit more employed as people will/ do have less money for panel change outs and rewires to comply with 210.12 ,... compliant creativity just might get you the job:smile:
 

donselectric

Senior Member
Location
nh
i was looking in feeders ,min size in the 02 code.
i didn't think you could run less then 10"s to feed any sub.
at least thats what I've always done....
 