- Illinois
- retired electrician
I don't see how you can read 430.62(A) as supplying anything other than motor loads. The language is very specific as feeder is modified by "supplying a specific fixed motor load(s).I am not sure how you get that?
430.62(A) A feeder supplying a specific fixed motor
load(s) and consisting of conductor sizes in accordance with 430.24
shall be provided with a protective device having a rating
or setting not greater than the largest rating or setting of the
branch-circuit short-circuit and ground-fault protective device
for any motor supplied by the feeder [based on the maximum
permitted value for the specific type of a protective device in
accordance with 430.52, or 440.22(A) for hermetic refrigerant
motor-compressors], plus the sum of the full-load currents of
the other motors of the group.
The high-level object is a "feeder"
"supplying a" is inclusive, not exclusive.
Then referencing "430.24 Several Motors or a Motor(s) and Other Load(s) ", is a inclusive relative clause since 430.24 is included this "feeder" might carry more than just motors.
Then the terms "specific" and "fixed" are adjectives that function as prenominal modifiers for the noun "motor." not the feeder it can really be any feeder that supplies a fixed motor.
If that is what it was intended to mean there would be no reason for 430.63 to exist.