I recently went to work for a EC that uses #14 for switch legs on a 20 amp circuit . Is there anywhere in code that allows this? Eddie
240.4(D) leases no wiggle room on this at all.![]()
240.5 (B)(2) Fixture Wire
Fixture wire shall be permitted to be tapped to the branch circuit conductor or a branch circuit in accordance with the following:
240.4 (E) Tap Conductors
Tap conductors shall be permitted to be protected against overcurrent in acordance with the following:
(2) 240.5(B)(2) Fixture wire
240.5 (B)(2) Fixture Wire
Fixture wire shall be permitted to be tapped to the branch circuit conductor or a branch circuit in accordance with the following:
(1) 20-ampere circuits - 18 AWG and larger up to 50' of run length
(2) 20-ampere circuits - 16 AWG and larger up to 100' of run length
(3) 20-ampere circuits - 14 AWG and larger
(4) 30-ampere circuits - 14 AWG and larger
(5) 40-ampere circuits - 12 AWG and larger
(6) 50-ampere circuits - 12 AWG and larger
I'm not saying I do this myself. Just brought this up for discussion. Based on 2005 NEC.
When would you have a fixture wire longer than 100'? That could be a 10 story down rod?
iWire,
What is your take on using #14 as a tap from a #12 circuit,
for the purpose of attaching a Receptical?
Why is the legnth listed up to 100' in (2) but the legnth unrestricted in (3).
When would you have a fixture wire longer than 100'? That could be a 10 story down rod?
iWire,
What is your take on using #14 as a tap from a #12 circuit,
for the purpose of attaching a Receptical?
I am not asking for a 'ruling', just a comment.
There is a significant difference: the 15a receptacle's rating is based on the slot shape (i.e., it rejects other plug configurations), not its electrical capacity.Personally, I think 'diversity' would lean in this direction,
just as justifying a 15Amp Receptical on a 20Amp circuit.