In the 2005 NEC, Table 210.24 it shows 14 ga. as being allowed for taps on 20 and 30 a circuits.
What would be some examples of these "taps"
Would pigtails on 15 a. receptacles be one?
Would pigtails on 15 a. receptacles be one?
..........What article disallows a 14 ga pigtail for a 15 a receptacle on a 20 a. circuit?
Because a genuine tap has a known and controllable load limiting, whereas a receptacle can easily be loaded to (or beyond) the circuit's ampacity or OCP.I think you can do that in lighting, but why wouldn't a pigtail for a 15 a receptacle qualify as well? Why would a pigtail not be a tap?
How about 240.4(D)?What article disallows a 14 ga pigtail for a 15 a receptacle on a 20 a. circuit?
I would expect you could tap a #14 to a 20 or 30 amp circuit if you ran the tap first to a 15 amp fuse or CB before connecting it to a load.
I don't know. I suppose to continue would just be argumentative and pretty much pointless. Personally, I think 20 a. pigtails oughta be 12 ga. for the very reasons you stated.... but I really haven't seen anything that explains why table 210.24 shows 14 ga. taps allowed on 20 and 30 a circuits, and why a receptacle pigtail could not be considered a tap.
Maybe 210.24 oughta be modified.
Maybe I oughta be modified.:smile:
OP, It's funny even though you asked 3 times not one person can offer an explination of why table 210.24 says you can have a #14 tap on a 20a circuit or give an example...I can't either... I've gone around and around with this thing.
240.4(D) says you have to have a #12 on a 20a unless allowed by 240.4(E)....240.4(E)(3) says taps are ok IAW 240.21 (location in circuit)
240.21(A) says you can have branch circuit tap conductors IAW with 210.20.
210.20 (B) says conductors have to be protected IAW 240.4 (a big circle) but cords and fixtures have to be protected IAW 240.5 which actually does allow smaller gages per OCPD in comparison to 240.4(D)
But table 210.24 specifically calls out the fixture wires and cords are a separate issue than taps and circuit wires....so I don't get it.
I guess I'll just do what everybody else is doing and start saying "It's obvious...no #14 pigtails on 20a circuits duh! If you need me to explain it than I'm not going tell you!"
Hey don't I get a bucket of chicken mailed to my house for my 1000th post?
OP, It's funny even though you asked 3 times not one person can offer an explination of why table 210.24 says you can have a #14 tap on a 20a circuit or give an example...I can't either... I've gone around and around with this thing.
240.4(D) says you have to have a #12 on a 20a unless allowed by 240.4(E)....240.4(E)(3) says taps are ok IAW 240.21 (location in circuit)
240.21(A) says you can have branch circuit tap conductors IAW with 210.20.
210.20 (B) says conductors have to be protected IAW 240.4 (a big circle) but cords and fixtures have to be protected IAW 240.5 which actually does allow smaller gages per OCPD in comparison to 240.4(D)
But table 210.24 specifically calls out the fixture wires and cords are a separate issue than taps and circuit wires....so I don't get it.
I guess I'll just do what everybody else is doing and start saying "It's obvious...no #14 pigtails on 20a circuits duh! If you need me to explain it than I'm not going tell you!"
Hey don't I get a bucket of chicken mailed to my house for my 1000th post?
What's the difference between a pigtail and the rest of the circuit conductor?
Mike Holt has said 210.19(A)(2) prevents using 14 AWG pigtails to receptacles and up to this morning I have agreed with that.
But while thinking on this thread and looking at 210.19(A)(2) I am not so sure it does prevent using 14 AWG pigtails on 20 amp circuits.
It says the conductors shall not have an ampacity less then that of a the branch circuit rating ......... but even 14 AWG TW is rated 20 amps.
Mike Holt has said 210.19(A)(2) prevents using 14 AWG pigtails to receptacles and up to this morning I have agreed with that.
But while thinking on this thread and looking at 210.19(A)(2) I am not so sure it does prevent using 14 AWG pigtails on 20 amp circuits.
It says the conductors shall not have an ampacity less then that of a the branch circuit rating ......... but even 14 AWG TW is rated 20 amps.
The problem that will occur over time is when the outlet is overloaded the 14 will have the insulation harden and fall off causing an eventually failure in the circuit that could lead to a fire,
This is not just my opinion it is a situation I see frequently in older homes.
240.4(D) unless there is a specific article allowing you to ignore 240.4(D)
In the 2005 NEC, Table 210.24 it shows 14 ga. as being allowed for taps on 20 and 30 a circuits.
What would be some examples of these "taps"
Would pigtails on 15 a. receptacles be one?
14 AWG is rated 20 amps, it can handle 20 amps and the NEC allows us to use it for 20 amps for many items.
I think you have come up with the wrong reason for what you are seeing.
Like 240.4(E)?[/QUOTE]
I don't see receptacles on the list in 240.4(E) :smile: Maybe I'm not reading something into the post that is not there, just saying your hard pressed to show that you can ignore the limit of a 15 amp breaker on a #14 wire in a multi receptacle branch circuit.