240.21(B) has most of the tap rules.
Pigtails are not taps.
I take exception to the above.
Table 210.24 specifically allows "taps" of #14 wire on 15A, 20A and 30A circuits. We have used "pigtails" of #14 on 20A circuits for as long as I have
been in the trade (38 years), and have also called them taps.