Do some municipalities require #12 as the minimum regardless of what load it's serving?
Do most contractors here who mainly do residential work use #14 for general purpose receps and lighting? Do some municipalities require #12 as the minimum regardless of what load it's serving?
I don't think so. Consider the case of a house system where the service consists of a small pole mount xfm, long small wires from the xfm to the house panel, all circuits in the house originate from the panel.... Is the vac that is plugged into a general purpose 15A bedroom circuit any worse because it's 14awg? .
Old days: 12 for receptacles and 14 for indoor lighting.
New days: 14 anyplace allowed and 12 only where required.
Residential:
12# everything
Exception: 14# 250V 15A receptacles and low current 250V radiant ceiling circuits
Please provide more information. I am not familiar with these applications.
I have several 250V 50Hz German appliances and tools. I change the plugs from Schuko to NEMA 6-15 (250V 15A) and put in 250V 15A receptacles in several places.
210.6 Branch-Circuit Voltage Limitations. The nominal
voltage of branch circuits shall not exceed the values permitted
by 210.6(A) through (E).
(A) Occupancy Limitation. In dwelling units and guest
rooms or guest suites of hotels, motels, and similar occupancies,
the voltage shall not exceed 120 volts, nominal, between
conductors that supply the terminals of the following:
(2) Cord-and-plug-connected loads 1440 volt-amperes,
nominal, or less or less than 1?4 hp
I will second that......#14.....cheaper, and a lot easier to work with. I use it anywhere I can get away with it.....
it's easier to lasso and work with, but it sucks when a customer wants to plug in a
larger load.... so i use #12 for all receptacles, and #14 for all lights, etc.
with LED lighting becoming commonplace, you can put an awful lot of 5 watt led's
on a single circuit.... most of them with the power supply only draw about 15 watts.
What single appliance load would exceed the capacity of a 15amp circuit? Especially in a residential setting?
BTW: I typically install a 20 amp circuit in the garage, in case they use a compressor or table saw.