is it code to have a #14 pigtail in an outlet box that has #18 wire and is on a 20 amp circuit ? article number ?
is it code to have a #14 pigtail in an outlet box that has #18 wire and is on a 20 amp circuit ? article number ?
#18 wire? what is the voltage? is the #18 on a 20 amp breaker?
is it code to have a #14 pigtail in an outlet box that has #18 wire and is on a 20 amp circuit ? article number ?
Whether you meant #12 wire on the 20a or not, no, 14ga pigtails are not permitted. They're part of the branch circuit wiring, all of which must be sized per the breaker (or vice versa, actually.)is it code to have a #14 pigtail in an outlet box that has #18 wire and is on a 20 amp circuit ? article number ?
What does voltage have to do with the fact that #18 is on a 20a breaker?
.