per nec 210.19a2 #14 tails should not be used on a 20a. multioutlet branch circuit, correct?
Correct. They're circuit conductors, and must be sized as such.per nec 210.19a2 #14 tails should not be used on a 20a. multioutlet branch circuit, correct?
tails from wirenuts to receptacle