Hello,
I still have a hard time believing that 15A outlets are allowed on a 20A circuit, provided 12 awg is used due to my applying reason to the English language.
I understand that apparently 15A outlets (duplex receptacles) are identical to 20A outlets except that they lack the faceplate that would allow 20A-style plugs to be inserted, and that a 15A outlet has a 20A pass through rating.
My example is a residential kitchen counter where a 15A GFCI feeds four 20A outlets on a 20A circuit. 12 awg is used.
1. Is this correct?
2. Is this a best practice?
3. Could not, for example, a power strip be plugged into a 15A outlet with a load of more than 15A and not trip the 20A breaker, thus becoming a hazard? (And yet the installation of 15a outlet on 20a circuit was ‘correct’?)
4. Why do 20 amp outlets (duplex recepacles) exist if 15A outlets are rated for 20A?
Thank you
I still have a hard time believing that 15A outlets are allowed on a 20A circuit, provided 12 awg is used due to my applying reason to the English language.
I understand that apparently 15A outlets (duplex receptacles) are identical to 20A outlets except that they lack the faceplate that would allow 20A-style plugs to be inserted, and that a 15A outlet has a 20A pass through rating.
My example is a residential kitchen counter where a 15A GFCI feeds four 20A outlets on a 20A circuit. 12 awg is used.
1. Is this correct?
2. Is this a best practice?
3. Could not, for example, a power strip be plugged into a 15A outlet with a load of more than 15A and not trip the 20A breaker, thus becoming a hazard? (And yet the installation of 15a outlet on 20a circuit was ‘correct’?)
4. Why do 20 amp outlets (duplex recepacles) exist if 15A outlets are rated for 20A?
Thank you