Today I was dinged for having a 15 amp duplex gfci receptacle on a dedicated 20 amp breaker. I am trying to find the requirement which calls for a 20 amp gfci on a 20 amp breaker in the code and seem to be having serious brain fade. Where is that found in the NEC?
 
Today I was dinged for having a 15 amp duplex gfci receptacle on a dedicated 20 amp breaker. I am trying to find the requirement which calls for a 20 amp gfci on a 20 amp breaker in the code and seem to be having serious brain fade. Where is that found in the NEC?


You cant find whats not there. Tell mr inspector to site the number. Its a duplex so not a single receptacle, its 2 receptacles.
 
today i was dinged for having a 15 amp duplex gfci receptacle on a dedicated 20 amp breaker. I am trying to find the requirement which calls for a 20 amp gfci on a 20 amp breaker in the code and seem to be having serious brain fade. Where is that found in the nec?

210.21(b)(3).
 
210.21 (b)(3) table That's what I was looking for. The only thing, because it is a duplex does this chart not allow a single 15 amp gfci duplex receptacle to be installed on a dedicated 20 amp circuit? The way I interpret this code is it is completely allowable.
 
magictolight.com,

I personally agree with your understanding. A duplex is two receptacles and two 15 amp receptacles are permitted to be fed from a 20 amp circuit...

mweaver
 
Last edited:
Interesting. However, where I get caught up is definitions calls a receptacle "a contact device installed at the outlet for the connection of an attachment plug. A single receptacle is a single contact device with no other contact device on the same yoke. A multiple receptacle is two or mor contact devices on the same yoke." When considering this, by golly, I think I may have caught the inspector. What do you think?
 
magictolight.com,

(for me...)
When you install a duplex receptacle you do in fact install two contact devices at the outlet for the connection of two attachment plugs.

…but rather than say: “I think I may have caught the inspector” … I (personally) prefer to use the thinking that you may have the opportunity to expand his understanding of this requirement :)

mweaver
 
Last edited:
Today I was dinged for having a 15 amp duplex gfci receptacle on a dedicated 20 amp breaker. I am trying to find the requirement which calls for a 20 amp gfci on a 20 amp breaker in the code and seem to be having serious brain fade. Where is that found in the NEC?

if you have only one device on a 20a. ckt, that device must be 20 amp, correct?

that's probably where your inspector is coming from.

the difference between a 15 amp and a 20 amp gfci is something like $4.....?
 
"the difference between a 15 amp and a 20 amp gfci is something like $4.....?"

Unfortunately I was working 100 miles from nowhere and all I had was 15 amp gfci receptacles.
I have a call into the inspector and as soon as he gets back to me i will post his reply.
 
definition of receptacle is "a contact device installed at the outlet for the connection of an attachment plug. A single receptacle is a single contact device with no other contact device on the same yoke. A multiple receptacle is two or mor contact devices on the same yoke." 210.21(B)(1) This section refers to single receptacles specifically.
 
Last edited:
Well, the inspector got back to me. He said, "I probably should have stated that better. When I saw the 15 amp gfci i assumed that you used 14 gauge wire. I did not open it up to check. You can have one 15 amp gfci on a 20 amp circuit because it has two plugs."

So maybe I made something out of nothing but I do appreciate the conversation!
 
Well, the inspector got back to me. He said, "I probably should have stated that better. When I saw the 15 amp gfci i assumed that you used 14 gauge wire. I did not open it up to check. You can have one 15 amp gfci on a 20 amp circuit because it has two plugs."

So maybe I made something out of nothing but I do appreciate the conversation!

You see. Inspectors are human-- at least, I think they are. :D
 