I have a client that wants / insists we use 14 GA wire and 15 AMP breakers in their retail restaurant space due to 5 of 35 light fixtures they need. Why and how do I tell him we cannot and should not do this?
Welcome to the forum.Why and how do I tell him we cannot and should not do this?
I'm generally running 14 AWG to such luminaires in most cases.The light fixtures are most likely LED, so a 15 amp circuit would most likely be more than sufficient. I’m betting the fixtures have their own j-box, and are not rated for #12 wire. The manufacturers get away with extremely small boxes that also contain the drivers.
Prohibit all 15A circuits or just on circuits supplying general use 120 volt receptacle(s)?I believe that places like NYC prohibit 15A circuits in commercial. Could be a local amendment where he is?
-Hal
There is no prohibition on 15 amp circuits. Back 20 years ago the old NYC electrical code prohibited 20 amp general lighting and receptacle circuits. 277 volt lighting circuits were then 20 amp circuits as were individual branch circuits and SABC's. Since NYC has a minimum branch circuit conductor size of #12 using 15 amp circuits really make no sense.Prohibit all 15A circuits or just on circuits supplying general use 120 volt receptacle(s)?
Here in the city you can use a 15A OCPD, some appliances require it you just can't use 14 AWG wire, 12AWG is the minimum size.I believe that places like NYC prohibit 15A circuits in commercial. Could be a local amendment where he is?
-Hal
Some product listings require a 15A OCPD, such some bath fans, LED drivers and recently to my surprise a ductless heatpump required a 2 pole 15.Since NYC has a minimum branch circuit conductor size of #12 using 15 amp circuits really make no sense.
So, you might as well use a 20A breaker to feed it, unless there is a reason not to. So, in effect 15A circuits are not used.Since NYC has a minimum branch circuit conductor size of #12
So they basically banned 14 AWG.There is no prohibition on 15 amp circuits. Back 20 years ago the old NYC electrical code prohibited 20 amp general lighting and receptacle circuits. 277 volt lighting circuits were then 20 amp circuits as were individual branch circuits and SABC's. Since NYC has a minimum branch circuit conductor size of #12 using 15 amp circuits really make no sense.
I was going to ask if fixture whips/taps are still allowed. Curious what the actual wording is.So they basically banned 14 AWG.
I hope they at least still allow it or smaller for limited power circuits like controls and such.
Controls yes, for branch circuits, no.So they basically banned 14 AWG.
Yes more like never allowed it, its been cited as the reason for fewer AFCI requirements.So they basically banned 14 AWG.
The NYC amendment to 210.24 sums it up:I was going to ask if fixture whips/taps are still allowed.
Remember don't lump the old firealarm circuits with controls they need to be 12 also.Controls yes, for branch circuits, no.
AFCI requirements is another ball game, but assuming they do what they claim they will do I don't see why conductor size would make a difference in why you should or should not require AFCI protection. You still can plug in a 18-2 lamp cord into a receptacle circuit that has 12 AWG branch circuit conductors or maybe even 10 AWG for voltage drop reasons.Yes more like never allowed it, its been cited as the reason for fewer AFCI requirements.
Replace the value “14” that appears twice in the column headed 15A, and once
each in the columns headed 20A and 30A in the Circuit Rating Section with the value “12.”
There is no amendment to 240.5 for fixture wires and controls.
Any other place in the code where it says #14 minimum its changed to #12.