hardworker
Senior Member
What is the theory and code behind using the standard 15 amp receptacle on a 12 awg 20 amp breaker protected circuit? It seems to me the 15 amp receptacle is the weak spot.
What is the theory and code behind using the standard 15 amp receptacle on a 12 awg 20 amp breaker protected circuit? It seems to me the 15 amp receptacle is the weak spot.
Have you ever tried to intentionally overload one to see if it trips? Some may just have a switch with no overcurrent protection at all. In fact most with a rocker style switch likely are just switches in most cases I think, those with a pop out button style breaker - obviously have overcurrent protection.Power strips have a built-in breaker to limit the maximum current.
Have I ever seen one trip? Nope.
According to the person tasked with health and safety at my workplace, all power strips MUST have overcurrent protection. The little rocker switch is in fact a circuit breaker that will trip if overloaded.
That said, I've never understood the need for an OCPD on a power strip. If it's plugged into a 15A receptacle on a 15A circuit, just build it to be able to handle 15A. If you really want to be conservative, build it to handle 20A. Ahhhh, the logic of UL....
SceneryDriver
The little rocker switch is in fact a circuit breaker that will trip if overloaded.
SceneryDriver