A GC informed me that a job of his (not mine) failed inspection because the EC installed 15a recepts on 20a circuits. Although this is not something I would do...where is the vio?? I always refer to 210.21 (B)(3). I cant find the vio anywhere else. Most likely an AHJ.
Anyone know anywhere that this is a vio??
Once again:
20a recepts not allowed on 15a circuits, but 15a recepts allowed on 20a circuits per 210.21(B)(3).
Thanks in advance.
Anyone know anywhere that this is a vio??
Once again:
20a recepts not allowed on 15a circuits, but 15a recepts allowed on 20a circuits per 210.21(B)(3).
Thanks in advance.