A GC informed me that a job of his (not mine) failed inspection because the EC installed 15a recepts on 20a circuits. Although this is not something I would do...where is the vio?? I always refer to 210.21 (B)(3). I cant find the vio anywhere else. Most likely an AHJ.
Anyone know anywhere that this is a vio??
Once again:
20a recepts not allowed on 15a circuits, but 15a recepts allowed on 20a circuits per 210.21(B)(3).
Thanks in advance.
Before you judge the Inspector decision asks yourself if you look the notes on approved plans for this project. It's a very common variance for commercial projects to place a note under condition to the job (specially a commercial one). Those notes are insert by EE assign to the project and like it or not you have to follow up.