wbalsam1
Senior Member
- Location
- Upper Jay, NY
I have been successful in every attempt at coaxing electricians to NOT intermix conductor sizes. Each time that I inspect a job where the installer has used 14/3 travellers on a 12/2 circuit and intended to protect at 20 amps, I have been successful in having this installer remove the 14/3 and replace with 12/3 or remove the 12/2 and replace with 14/2 and protect at 15 amps. I make every effort to disallow this and the company I work for also does not permit this, as a company policy. Nearly everyone in the industry around here considers this intermixing to be a poor wiring method. :smile: