E Eric42 Member Jul 20, 2022 #1 If the motor control has a VSD do you still have to size your wire at 125% . It is for an air compressor - 150 hp 480v 210 fla
petersonra Senior Member Location Northern illinois Occupation Semi-retired engineer Jul 20, 2022 #2 Eric42 said: If the motor control has a VSD do you still have to size your wire at 125% . It is for an air compressor - 150 hp 480v 210 fla Click to expand... wiring to the VFD has to be 125% of the rated input current of the drive. wiring from the vfd to the motor is just normal motor wiring. 125% of the FLC from the tables in the NEC.