Hello!
I am supposed to order all materials for a compressor install and have encountered 3 different specs for wire size. This is a Kaeser DSD 150--150 HP, 460 V, 3 PH Motor with and FLA of 225 Amps.
Using the code calcs I found that I should use a 4/0 AWG wire for power. This was the same on the SquareD slide rule motor calculator I used.
I also have an SPD Bussmann Electrical Protection Handbook that says I need 350 kcmil wire for power. This figure is closer to the manufacturers recommendation of 400 kcmil wire.
I want to believe the manufacturer but with all the other calculations, 400 kcmil wire almost seems like overkill but I am really not sure. I was taught low voltage process control in school and this is slightly out of my educational capacities. I don't want to screw anything up and I want to save the company money at the same time. I know that bigger equals more expensive and if 400 kcmil wire is not necessary I would like to use something smaller. I just don't understand why there would be such a big difference in wire sizing.
I would appreciate any help with this.
I am supposed to order all materials for a compressor install and have encountered 3 different specs for wire size. This is a Kaeser DSD 150--150 HP, 460 V, 3 PH Motor with and FLA of 225 Amps.
Using the code calcs I found that I should use a 4/0 AWG wire for power. This was the same on the SquareD slide rule motor calculator I used.
I also have an SPD Bussmann Electrical Protection Handbook that says I need 350 kcmil wire for power. This figure is closer to the manufacturers recommendation of 400 kcmil wire.
I want to believe the manufacturer but with all the other calculations, 400 kcmil wire almost seems like overkill but I am really not sure. I was taught low voltage process control in school and this is slightly out of my educational capacities. I don't want to screw anything up and I want to save the company money at the same time. I know that bigger equals more expensive and if 400 kcmil wire is not necessary I would like to use something smaller. I just don't understand why there would be such a big difference in wire sizing.
I would appreciate any help with this.