150 kva transformer 3phase 480 volt to 120/208 2005 nec
grumpy11
i have to give a customer a full 400amps at 208 volts 3 phase 4 wire.
the design is to install a 150kva step down transformer.
now since a 150kva tx. on the primary is 180amps i intend on running 3#3/0 fused at 180 amps
off the secondary side i believe {using 90degree wire }i should use 750 mcm
since i am going into a 400amp switch
750mcm at 90degree the amp rating is 535
since it 4 wire and derating at 80%
i believe it should be 535 x 0.80 x0.91{derating of 90 degree wire} i come up with 390 amps.
am i on the right track.
yes the gec is based on 250.66 and egc is based on 250.122
Just some quick thoughts
180 is too low on the primary, you may have trouble energizing the transformer due to inrush. Use at least a 225 and as high as 450, the conductors would have to exceed the overcurrent device rating you chose.
On the secondary I would likely go with two sets of 3/0s for 400 amps but if you want to provide a 'full 400 amps' continuously you need to use a 500 amp breaker / panel / conductors instead of the 400 amp set up.
With a 390 amp ampacity you cannot use a 400 amp OCPD on the secondary condcutors. Why are you considering the neutral as a CCC is the transformer load more than 50% non-linear?
150kva transformer
150kva transformer
ok i could see the error in the primary i forgot to look at table 450.3{b}
on the secondary i think 3/0 is to small with derating and all that
i dont think i want to run pararell sets
as Rob noted, I see no reason for you to consider the neutral as a current carrying conductor. Are you looking at the 400 amp load as continuous ?
150 kva transformer
150 kva transformer
i dont know if the load is going to be continuous for more them 3 hours .
lets say it is
but doesnt article 310.15 4 c tell you to consider a neutral a current carrying conductor
More specifically it states:
(c) On a 4-wire, 3-phase wye circuit where the major portion of the load consists of nonlinear loads, harmonic currents are present in the neutral conductor; the neutral conductor shall therefore be considered a current-carrying conductor.
It is highly unlikely that the MAJOR portion of the load is non-linear
That said, your 150 kva transformer has an output of 416 amps with 25% allowing 520 amps so you could easily go to a 500 amp secondary (legally higher) and use 900 kcmil but that would be a monumental task. Most everyone would parallel 250 kcmil.
I would agree with the primary OCPD sizing, but I see no reason the conductors would have to exceed the ocpd device rating. If a 450A primary OCPD was used, the conductors could be 600MCM, or use 500MCM with a 400A primary OCPD, etc. The "next standard size up" would be applicable for primary OCPDs rated 800A or less.