Hi Everyone,
I did the online search to find a forum to discuss 1500VDC rated AFCI device on ground mount project, and I found this! Glad to be here. I am looking forward to learn and contribute. Here is what I am evaluating and could use your opinions and practical experience. I am working on a design of a large ground mount solar farm (>15MW DC) with 1500VDC UL listed central inverters. PV modules and combiner boxes are also UL listed for 1500VDC. The design is at 90PCT stage. The implemented code cycle for the AHJ is NEC2014.
NEC 2014 690.11 requires AFCI devices for all systems greater than 80VDC . My research tells me that 1500VDC device AFCI is some what of a "purple cow
". Digging down further I could come up with 2 options
- Per NEC 90.4, maybe get a waiver for AFCI protection for this project if AHJ chooses to refer to NEC 2011; which requires AFCI protection only for PV systems located on "Buildings" under the basis that product UL safety standard does not exist.
- Go with NEC 2017 and follow 690.11 exception. Please note that the system is located on a site where excavation is not allowed, (the design currently has ladder tray) than option is to go with enclosed cable tray - which is adding cost and design change to the project.
I have not made a final decision to either go in with a request for waiver to AHJ or provide enclosed cable tray for the whole system. I am evaluating construction feasibility for enclosed cable tray and the risk of not having AFCI on the ground mount array.
How has your experience been for satisfying 690.11 requirement for 1500 VDC PV Systems? Thanks
I did the online search to find a forum to discuss 1500VDC rated AFCI device on ground mount project, and I found this! Glad to be here. I am looking forward to learn and contribute. Here is what I am evaluating and could use your opinions and practical experience. I am working on a design of a large ground mount solar farm (>15MW DC) with 1500VDC UL listed central inverters. PV modules and combiner boxes are also UL listed for 1500VDC. The design is at 90PCT stage. The implemented code cycle for the AHJ is NEC2014.
NEC 2014 690.11 requires AFCI devices for all systems greater than 80VDC . My research tells me that 1500VDC device AFCI is some what of a "purple cow
- Per NEC 90.4, maybe get a waiver for AFCI protection for this project if AHJ chooses to refer to NEC 2011; which requires AFCI protection only for PV systems located on "Buildings" under the basis that product UL safety standard does not exist.
- Go with NEC 2017 and follow 690.11 exception. Please note that the system is located on a site where excavation is not allowed, (the design currently has ladder tray) than option is to go with enclosed cable tray - which is adding cost and design change to the project.
I have not made a final decision to either go in with a request for waiver to AHJ or provide enclosed cable tray for the whole system. I am evaluating construction feasibility for enclosed cable tray and the risk of not having AFCI on the ground mount array.
How has your experience been for satisfying 690.11 requirement for 1500 VDC PV Systems? Thanks