techtonix
Member
- Location
- Bisbee, Az
I am writing this question because of how the combination Load Center didn't pass through Inspection with my local utility due to the manufacturer's inconsistency in marking and labeling, let me explain... The SquareD 150 Amp load center (SC816F150PS) shares the same body as the 200 Amp model SC816F200PS. On the body itself the load center is listed at 200 Amps, however the permanently / factory installed main breaker is rated at 150 Amps as the serial number and description also agree with. Because the main breaker and serial number say 150 amps and because this is what I pulled a permit for, I sized the overhead conduit and wiring to 1.5" dia which is appropriate as per their specs. The utility inspector saw the 200 amp rating on the body of the box and failed the inspection stating that the conduit should be 2"dia, meaning I would have to buy entirely new hardware and copper wiring throughout, having me re-do everything costing me easily $300 and setting construction back two weeks, all because of combined and economized factory specs. City and utility inspectors can't even agree on this and I'm stuck with a residential construction site with no electricity. So what gives, which inspector is right?