Correct, no shielding is required for soft starters. Once it is done ramping, it is bypassed and the motor is running across the line. Shielding for VFD cables is sometimes required, but never for soft starters. That demonstrates a basic lack of understanding of the technology on their part.I’m using the 2023 Code. Id love to be able turn this into an outright code violation.
Routing 5kV, shielded 133% into a 460V motor peckerhead has many problems - where/how do they terminate the shields?
There’s no room for that. Also the cable OD is so large it won’t even fit into the threaded hub. And lastly all resources I’ve found show no shielding is required on a soft start