I have what may be a stupid question.
Here is my situtation. I am living in Brazil and involved with a American Co. that supplies housing. Brazilian power is 220v/60hrzt phase to neutral, so they transform it to 120v phase to neutral so that U.S. purchased equipment works and the employee does not need to use small transformers all over the house. One of the permenatly owned houses is going through a major renavation, including the electrical system. They will be using localy purchased componets which are slightly diffrent from the U.S..
Here is the problem/question: They plan calls for a general purpose branch circuit to one room with 4mm(eqiv. to #10) wire protected by a 25a breaker to feed recepticles with 10a/15a 250v stamped on the face by the manufacturer. I know what the NEC states about branch circuits ampacities, but I would like to know why it says what it says. Is there a danger to the residents or the appliance.
The wire is rated for the voltage and ampacity.
The recpticle is rated for the voltage. The only problem I see is the ampacity rating of the recptiles, and if the recpticles are rated for 25a with a nema15 layout is there still a problem.
By the way there are no codes here and/or formal training or certification programs. Anyone with a pair of Kleins and some 33 can claim to be a Electrician'
Thanks for the help
DJ Heroux
Here is my situtation. I am living in Brazil and involved with a American Co. that supplies housing. Brazilian power is 220v/60hrzt phase to neutral, so they transform it to 120v phase to neutral so that U.S. purchased equipment works and the employee does not need to use small transformers all over the house. One of the permenatly owned houses is going through a major renavation, including the electrical system. They will be using localy purchased componets which are slightly diffrent from the U.S..
Here is the problem/question: They plan calls for a general purpose branch circuit to one room with 4mm(eqiv. to #10) wire protected by a 25a breaker to feed recepticles with 10a/15a 250v stamped on the face by the manufacturer. I know what the NEC states about branch circuits ampacities, but I would like to know why it says what it says. Is there a danger to the residents or the appliance.
The wire is rated for the voltage and ampacity.
The recpticle is rated for the voltage. The only problem I see is the ampacity rating of the recptiles, and if the recpticles are rated for 25a with a nema15 layout is there still a problem.
By the way there are no codes here and/or formal training or certification programs. Anyone with a pair of Kleins and some 33 can claim to be a Electrician'
Thanks for the help