Gonna need some help on this one. I'm not too familiar with industrial machines so any advice would be greatly appreciated.
Customer bought a 15HP meat grinder and would like me to get it working. It currently has just an undersized cord with no plug cap on it. No motor starter, E-stop or anything. See pic. Will be feeding it with 240v 3ph.
This is the motor:
http://www.baldor.com/catalog/M2333T-9
He wants it cord and plug connected to allow for it to be moved and stored out of the way when not in use. My thought is mount a motor starter on the unit and include a on/off/jog on the motor starter. I will also have to mount an E-stop somewhere close the the business end. Is this the easiest way to do it? Is there a better way? Any suggestions on the E-stop?
Also, I haven't done motor sizing in many years and am a bit rusty. Here's what I came up with. Please let me know if I'm calculating it correctly:
FLC = 42a from table 430.250
BC breaker would be 42 x 250% max = 105a. Table 430.52. I would use a 60a breaker
BC conductors would be #6 CU - 42 x 125% = 52.5a 430.22
Motor starter would be a Nema 2 size
Heaters would be 42 x 125% = 52.5a 430.32(A)(1)
plug and receptacle would be 60a, horsepower rated. Any suggestions on this?
Thanks!
Customer bought a 15HP meat grinder and would like me to get it working. It currently has just an undersized cord with no plug cap on it. No motor starter, E-stop or anything. See pic. Will be feeding it with 240v 3ph.
This is the motor:
http://www.baldor.com/catalog/M2333T-9
He wants it cord and plug connected to allow for it to be moved and stored out of the way when not in use. My thought is mount a motor starter on the unit and include a on/off/jog on the motor starter. I will also have to mount an E-stop somewhere close the the business end. Is this the easiest way to do it? Is there a better way? Any suggestions on the E-stop?
Also, I haven't done motor sizing in many years and am a bit rusty. Here's what I came up with. Please let me know if I'm calculating it correctly:
FLC = 42a from table 430.250
BC breaker would be 42 x 250% max = 105a. Table 430.52. I would use a 60a breaker
BC conductors would be #6 CU - 42 x 125% = 52.5a 430.22
Motor starter would be a Nema 2 size
Heaters would be 42 x 125% = 52.5a 430.32(A)(1)
plug and receptacle would be 60a, horsepower rated. Any suggestions on this?
Thanks!