Depends on the starter.
Or put another way, RTFM...
Depends on the starter.
Or put another way, RTFM...
BTW....... I tend to stay away from IEC rated starters. They have a shorter life then NEMA gear.
I have come to the conclusion electricians do not like IEC but they have no problem going with Definite Purpose devices. Small size, limited life, and cheap components must not really be the issue.
As far as automatically up sizing the overload - Please don't. Instead, read the instructions that need to be followed (some manufacturers included a SF adjustment when they came up with their sizing table).
Read The <Factory> Manual :angel:RTFM????? You might have to elaborate on that one. I don't see it defined in Art. 100
Read The <Factory> Manual :angel:
With NEMA starters with thermal overload elements, the proper way to size the elements is to use the proper selection table published by the manufacturer. For single enclosed starters the applicable table often is a label attached to the enclosure somewhere but you can also find selection tables in their product catalog. To find the correct table you need starter series information, number of thermal overloads that will be used, and other information on the enclosure as well as whether or not there is other heat producing components in the enclosure.If the OP uses a NEMA starter with bi-metallic OL s. Shouldn't he take the FLA and multiple it by the service factor of the motor (usually 1.15) to size the OLs.
BTW....... I tend to stay away from IEC rated starters. They have a shorter life then NEMA gear.
Glad to see you got some clarity on those issues.
So are you good on the electrical aspect now?
Your 60 amp breaker may not hold for startup. 42 x 2.5 = 105 not 60.Yes. I didn't hear any arguements against my calculations, outside of the heaters, so I must have done them correctly. Thank you all for the assistance.
Install a vfd for this application.