15kV feeder over building roof

Status
Not open for further replies.

winslowfam

Senior Member
Location
VA
Hi, looking for code issues with running 15kV feeder from company-owned switchyard, over the roof of an existing plant building in conduit, to feed another building being erected. All I have found is a reference to running service over building, which is allowed if properly suppported. Thanks.
 
Re: 15kV feeder over building roof

Probably fine. But you are probably talking about a feeder instead of a service.
 