kingpb
Senior Member
- Location
- SE USA as far as you can go
- Occupation
- Engineer, Registered
So, I have heard of this, but never actually seen it, or has it ever been proposed to me by a manufacturer before, but honestly, never needed 4000A MV gear either. Always stayed within 3000A.
I need a 4000A 13.8KV bus. In lieu of using a single 4000A breaker, which requires fan cooling, the manufacturer has proposed using 2 x 2000A breakers in parallel that don't require fan cooling. Fault current will be controlled by the transformer impedance ahead of it, to keep it within short circuit ratings.
Looking for pros/cons.
I need a 4000A 13.8KV bus. In lieu of using a single 4000A breaker, which requires fan cooling, the manufacturer has proposed using 2 x 2000A breakers in parallel that don't require fan cooling. Fault current will be controlled by the transformer impedance ahead of it, to keep it within short circuit ratings.
Looking for pros/cons.