15kva xfmr
hhsting
Glen bunie, md, us
Junior plan reviewer
15kva 480V to 208/120V three phase transformer does system bonding jumper and bonding jumper to enclosure provided by manufacturer or contractor has to provide?
infinity
New Jersey
Journeyman Electrician
I have never seen a 15 kva transformer with a factory bonded X0 so it would be field installed.
DrSparks
The Everlasting Know-it-all!
Madison, WI, USA
Master Electrician and General Contractor
Depends on the manufacturer. New ones are now coming with a grounding/bonding terminal bar and a strap connected to the chassis. Some, you have to wire it up yourself. Check with your supplier.
Sent from my BE2028 using Tapatalk
DrSparks
Madison, WI, USA
Eh. I just realized how small we're talking. Yeah, not sure on that.
petersonra
Northern illinois
engineer
most small transformers I have used of late have a bonding terminal included attached to the sheet metal. but no bonding strap. having thought about it, I find that a little curious since almost always in 120V systems it will be required.