I got a question, are we talking about an HID installation, or are we talking about 1500 watt quartz fixtures?
If HID, in no way would I want to fire 24kw of HID lamps up all at once, the inrush, and start up current would bring even a 125 amp panel to it's knees.
also If they are MH, pulse start uses only half the current for start up, and less wattage can be used as they produce much more lumen's per watt then standard MH fixtures.
If 1500 watt quartz is the fixture, then I would try to talk them into using PS MH fixtures, as the wattage can be reduced to about a 10th of the power.
a 320 watt PS mh produces about 23k lumen's of light, which will exceed what a 1500 watt quartz fixture would produce.
How big is this tennis court?
If you have room for changes, you can offer the power savings of the HID over quartz. the only draw back is a PS MH has about a 2 minute re strike time, regular MH has up to a 5 minute re strike time.
But I have PS fixtures in service over 7 years and haven't had to replace one bulb, but a regular MH will last about 2 to 3 years. RUUD guarantees there bulbs for 5 years. This would be another advantage over quartz, as they are lucky to last a year.
Just some food for thought.
Ruud makes some really nice fixtures. Lamp life is a good point for MH vs quartz. If you have 1500W MH and a 1500W quartz would there be savings? Or were you thinking of reducing to 1000W MH.