richf

Member
Service required : 1600A
Transformer with metering attached is feeding a 1600A service. 4-4" non-metallic conduits have been installed. The question is wheather 2or3 sets of 4-500kcmil should be installed to meet code. How would you calculate it?
 
Re: 1600A service

If the service OCPD is a single 1600 amp device, then you will need 5 sets of 500kcmil. Four sets of 500 kcmil is only 1520 amps. If you only have the 4 raceways you could install eight 4/0s in each of the four raceways and have 1664 amps of wire or you could use eight 350 kcmil in each of three raceways and have 1680 amps. These assume that the grounded conductor is not required to be counted as a current carrying conductor.
Don
 
Re: 1600A service

I would think it would be simpler to use 4 sets of 600 kcmil.
I agree, it would be simpler to install 600's. But the 8 sets of 4/0 is actually less copper (each pair of 4/0 is about 423KCM instead of 600KCM) for about the same ampacity. Voltage drop would probably be less also.

Steve
 
Re: 1600A service

According to Article 310-16, 500MCM @ 90deg. cel. is good for 430 amps. This is why you probably had 4 sets of 4" installed. I think the 500MCM (4 sets) is good for you installation.
 
Re: 1600A service

Originally posted by jrcoles:
According to Article 310-16, 500MCM @ 90deg. cel. is good for 430 amps. This is why you probably had 4 sets of 4" installed. I think the 500MCM (4 sets) is good for you installation.
See 110.14(C) Termination provisions. The 90 degree rating will not be allowed to be used. :)
 
Re: 1600A service

Only if your terminations are rated raed for 70deg. switch gear and transformers have 90deg. termaination on them now. I would check your termination rating on your equipment.
 
Re: 1600A service

Medium voltage terminations have been rated 90C for some time; in fact, I can't remember when they weren't. That rating is buried in the IEEE standards though, not the UL standards. UL evaluates MV switchgear and Transformers to the IEEE standards as well as their own.

The Category Code almost all electrical equipment is evaluated to is AALZ, "Equipment for Ordinary Locations." That is the fundamental standard that Section 110.14(C) was based on. AALZ requires not only the terminal but the equipment it is installed in to be evaluated before a 90C terminal rating may be applied.

I did a quick scan in the UL (1558) and IEEE (C37.20.1) standards for low voltage switchgear and couldn't find 90C recognized for terminal ratings.

The search was by no means exhaustive, but I'm curious which manufacture is offering 90C rated terminals in their low voltage switchgear.

Why are so many electrical engineers in a rush to see how marginal their design can be in industrial applications? :( I believe the NEC is excessive in many places but conductor ampacities is generally not one of them. Frankly, I believe the reason we've gotten excessive in many other areas, is because conductor ampacities are often too marginal.

Edit added: Present company excepted, of course.

[ July 21, 2004, 03:05 PM: Message edited by: rbalex ]
 