Rick F
Member
- Location
- philly, pa
We have lunch trucks on a street where I work, the school supplies the power for the trucks.30amp 2pole breaker gfci. everything is done right electrically..
I'm getting 17amps or there abouts going back on the neutral of the panel inside this one truck. total of both legs are pulling around 22A
the panel is feeding 3 motors (compressor units for fridges) and maybe 120W equivalent in LED lights,
can someone please tell me why 17A are returning on a 22A draw?
I'm just trying to understand, the power factor of the motors can't be that bad. the compressors are like 3yrs old..any help understanding would be appreciated..
I'm getting 17amps or there abouts going back on the neutral of the panel inside this one truck. total of both legs are pulling around 22A
the panel is feeding 3 motors (compressor units for fridges) and maybe 120W equivalent in LED lights,
can someone please tell me why 17A are returning on a 22A draw?
I'm just trying to understand, the power factor of the motors can't be that bad. the compressors are like 3yrs old..any help understanding would be appreciated..