how many 18 thhn wire can we pull through 3/8 trade size flexible metal conduit
i did not find the answer hopefully somebody would
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Are you sure it is thhn. Art. 402 does not list it for thhn and I don't see #18 thhn anywhere else. I would call the manufacturer and get the area of the wire.

It looks like TFFN may be equivalent
 
Last edited:

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
I think it may be a trick question, the smallest THHN I am aware of is #14. When I use smaller single conductors I usually use TFFN

Roger
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Whoa, that took a long time to post, (I had a phone call) Dennis already had the answer.

Roger
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I think it may be a trick question, the smallest THHN I am aware of is #14. When I use smaller single conductors I usually use TFFN

Roger

I agree it looks that way. T402.3 lists all of the fixture wires and there is no #18 THHN. 310.104(A) says THHN starts at size #14.
 